Comments for Case POD2007-00113

Case Number:POD2007-00113
Case Name:Poplar Springs Baptist Church
Review Type:Revision - Previously Approved
Case Description:Poplar Springs Baptist Church
Parcel ID: 843-696-3185
5270 CHARLES CITY RD
Legal Description:ES CHARLES CITY RD AC 20.89 47 A2 4
Engineer/Applicant: CARTER DESIGN
Project Case Number:POD2007-00113 (There is 1 related case)
Project Name:POPLAR SPRINGS BAPTIST CHURCH

Note: The County of Henrico is not responsible for any information placed in the "Comments" field by the public.

POD2007-00113 - Poplar Springs Baptist Church - Revision - Previously Approved
Final Submission for Signature

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(8010) Application Received    01/08/2008 DONE  Welton, Pamela T. 
Comments:
--
(8015) Plans Routed for Signature  01/14/2008  01/14/2008 DONE  Welton, Pamela T. 
Comments:
--
(8120) DPW Signed FCP  01/14/2008 02/01/2008 01/17/2008 DONE  Priestas, Lee 
Comments:
PreCon maybe scheduled
(8130) DPU Signed FCP  01/14/2008 02/01/2008 01/22/2008 APPR Clark, John 
Comments:
--
(8150) Planning Department Signed FCP  01/11/2008  01/11/2008 APPR  Pambid, Lee 
Comments:
Signed by Jim Strauss and routed to DPU 1/14/08

POD2007-00113 - Poplar Springs Baptist Church - Revision - Previously Approved
General Menu

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(A010) Application Received    06/08/2007   Welton, Pamela T. 
Comments:
--

POD2007-00113 - Poplar Springs Baptist Church - Revision - Previously Approved
Plan Review Menu

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(B005) POD-Original Review Initiated    06/13/2007 DONE  Welton, Pamela T. 
Comments:
--
(B115) Traffic Engineer Review  06/13/2007 06/29/2007 06/27/2007 CMTS  Jennings, Mike 
Comments:

PUBLIC WORKS - TRAFFIC ENGINEERING - JENNINGS, MIKE

will be attached to review engineer comments



(B120) DPW Review Engineer  06/13/2007 06/29/2007 03/24/2009  Bandura, Steve 
Comments:

PUBLIC WORKS - REVIEW ENGINEER - BANDURA, STEVE

_________

Please see the attached file(s) for more comments:
     ENG___Poplar_Springs_Baptist_Church___14jun07.DOC(Engr)
     ENV___Poplar_Springs_Baptist_Church___14jun07.DOC(Enviro)
     TRA_Popular_Springs_Baptist_Church_14JUN07.DOC(Traffic)
[Please Note: To view the file(s) you must have the correct software installed. If unable to obtain this, please contact the Reviewer or the Department of Planning for a hard copy of the comments.]

(B125) Environ Control Eng Rev  06/13/2007 06/29/2007 06/29/2007 CMTS Jackson, Scott 
Comments:

PUBLIC WORKS - ENVIRONMENTAL - JACKSON, SCOTT

See the DPW Review Engineer comment section for the Environmental
Division comment attachment.



(B135) Recreation & Parks Review  06/13/2007 06/29/2007 06/25/2007 CMTS Soldano, Mary Ann 
Comments:

REC & PARKS - SOLDANO, MARY ANN

Please see the attached file(s) for more comments:
     LP62207POD52_07PoplarSprings.DOC(POD52-07PoplarSprings)
[Please Note: To view the file(s) you must have the correct software installed. If unable to obtain this, please contact the Reviewer or the Department of Planning for a hard copy of the comments.]

(B140) VA Dept of Transport. Review  06/13/2007 06/29/2007 06/29/2007 DONE Greulich, Anthony 
Comments:
*Closed by Henrico IT Admin per Tony Greulich in Planning on 12/17/2015 04:46:10 PM*
(B145) VA Power Review  06/13/2007 06/29/2007 06/29/2007 DONE Greulich, Anthony 
Comments:
*Closed by Henrico IT Admin per Tony Greulich in Planning on 05/08/2017 10:56:53 AM*
(B150) Planning Review  06/13/2007 07/02/2007 04/02/2008 DONE  Pambid, Lee 
Comments:
--
(B30) Building Insp Rev  06/13/2007 06/29/2007 06/21/2007 CMTS  Gordon, Richard T 
Comments:
An accessible route shall be provided from the seating area to the chancel area.
An automatic sprinkler system shall be installed in accordance with NFPA 13 - 1999 edition.
The passenger loading zone located at plan west shall be accessible.
(B40) Fire Review  06/13/2007 06/29/2007 06/19/2007 CMTS  Rastegar, Abdol Russell 
Comments:

FIRE - RASTEGAR, RUSSELL

Hydrants must be within a 350-ft. hose lay of the building circumference, a minimum of 50 ft. from the structure wall and accessible to fire department apparatus. Measure hose as laid from apparatus.

Hydrants must be between 1 ft. and 7 ft. from the curb line and have 4 inch opening facing the street, unless otherwise instructed.

All structures must be accessible on all four sides to emergency equipment. A minimum of 20 ft. roadway width is required. A 150' hose from the apparatus must reach all points of the exterior of a building.

Additional Comments - Max hose lay shall not be more than 350 feet.
2- Please verify the location of the 3 FH required per ISO.



(B70) Police Review  06/13/2007 06/29/2007 07/02/2007 CMTS  Vann, Kimberly 
Comments:

POLICE - VANN, KIMBERLY

Please see the attached file(s) for more comments:
     Poplar_Springs_Baptist_7_07.DOC
[Please Note: To view the file(s) you must have the correct software installed. If unable to obtain this, please contact the Reviewer or the Department of Planning for a hard copy of the comments.]

POD2007-00113 - Poplar Springs Baptist Church - Revision - Previously Approved
FCP - Original Sub

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(D003) Orig Submission-FCP-Initiated     09/27/2007 DONE  Welton, Pamela T. 
Comments:
--
(D115) Traffic Engineer Review - FCP  09/27/2007 10/16/2007 10/17/2007 CMTS  Jennings, Mike 
Comments:

PUBLIC WORKS - TRAFFIC ENGINEERING - JENNINGS, MIKE

will be attached to review engineer comments



(D120) DPW Review Engineer - FCP  09/27/2007 10/16/2007 03/24/2009  Bandura, Steve 
Comments:

PUBLIC WORKS - REVIEW ENGINEER - BANDURA, STEVE

_________

Please see the attached file(s) for more comments:
     ENV___Poplar_Springs_Baptist_Church___28sep07.DOC(Enviro)
     ENG___Poplar_Springs_Baptist_Church___28sept07.DOC(Engr)
     TRA_Poplar_Springs_Baptist_Church_28SEP07.DOC(Traffic)
[Please Note: To view the file(s) you must have the correct software installed. If unable to obtain this, please contact the Reviewer or the Department of Planning for a hard copy of the comments.]

(D125) Environ Control Eng Rev - FCP   09/27/2007 10/16/2007 10/09/2007 CMTS Jackson, Scott 
Comments:

PUBLIC WORKS - ENVIRONMENTAL - JACKSON, SCOTT

See the DPW Review Engineer comment section for the Environmental
Division comment attachment.




(D130) Public Utilities Review - FCP  09/27/2007 10/16/2007 10/12/2007 TECH  Morton, Jarad 
Comments:

DPU - MORTON, JARAD

Please see the attached file(s) for more comments:
     Mathew_Schliske__Hyatt_Place___The_Shops___White_Oak_Village_JLM.DOC
[Please Note: To view the file(s) you must have the correct software installed. If unable to obtain this, please contact the Reviewer or the Department of Planning for a hard copy of the comments.]

(D150) Planning Review - FCP  09/27/2007 10/16/2007 10/31/2007 CMTS  Pambid, Lee 
Comments:
No additional comments
(D30) Building Insp Review - FCP  09/27/2007 10/16/2007 11/06/2007 DONE  Gordon, Richard T 
Comments:
--
(D40) Fire Review - FCP  09/27/2007 10/16/2007 10/02/2007 APPR  Rastegar, Abdol Russell 
Comments:

FIRE - RASTEGAR, RUSSELL

POD2007-00113 - Poplar Springs Baptist Church - Revision - Previously Approved
FCP - Final Submission (21)

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(G010) Rec from Developer FCP-F (21)    09/26/2007 DONE Moffett, Billy 
Comments:
--

*This site contains Comments made after February 1, 2007