Single Comment for POD2007-00113

Case Number:POD2007-00113
Case Name:Poplar Springs Baptist Church
Review Type:Revision - Previously Approved
Case Description:Poplar Springs Baptist Church
Parcel ID: 843-696-3185
5270 CHARLES CITY RD
Legal Description:ES CHARLES CITY RD AC 20.89 47 A2 4
Engineer/Applicant: CARTER DESIGN
Project Case Number:POD2007-00113 (There is 1 related case)
Project Name:POPLAR SPRINGS BAPTIST CHURCH

Note: The County of Henrico is not responsible for any information placed in the "Comments" field by the public.

DescriptionSubmission DateDue DateCompleted DateStatusReviewer
(B40) Fire Review  06/13/2007 06/29/2007 06/19/2007 CMTS  Rastegar, Abdol Russell 
Comments:

FIRE - RASTEGAR, RUSSELL

Hydrants must be within a 350-ft. hose lay of the building circumference, a minimum of 50 ft. from the structure wall and accessible to fire department apparatus. Measure hose as laid from apparatus.

Hydrants must be between 1 ft. and 7 ft. from the curb line and have 4 inch opening facing the street, unless otherwise instructed.

All structures must be accessible on all four sides to emergency equipment. A minimum of 20 ft. roadway width is required. A 150' hose from the apparatus must reach all points of the exterior of a building.

Additional Comments - Max hose lay shall not be more than 350 feet.
2- Please verify the location of the 3 FH required per ISO.