Case Number: | POD2007-00217 |
---|---|
Case Name: | Arco Iris Latino Mart |
Review Type: | Original Plan |
Case Description: | Arco Iris Latino Mart |
Parcel ID: | 773-747-8402 6111 STAPLES MILL RD |
Legal Description: | EL STAPLES MILL RD AC .864 97 B1 83 |
Engineer/Applicant: | BARTHOL DESIGN ASSOC |
Project Case Number: | POD2007-00217 (There are 6 related cases) |
Project Name: | ARCO IRIS LATINO MART |
Note: The County of Henrico is not responsible for any information placed in the "Comments" field by the public.
Description | Submission Date | Due Date | Completed Date | Status | Reviewer |
---|---|---|---|---|---|
(140) Division of Fire Review | CMTS | Rastegar, Abdol Russell | |||
Comments: FIRE - RASTEGAR, RUSSELL Hydrants must be within a 350-ft. hose lay of the building circumference, a minimum of 50 ft. from the structure wall and accessible to fire department apparatus. Measure hose as laid from apparatus. Additional Comments ADDITIONAL COMMENTS: 1- Please verify the location of the DFH for our review. 2- Please verify the location of the FDC for our review. 3- Please submit ISO Calculation to see how many FH is required. 4- Please show the location of FH. 5- Max. hose lay shall not be more than 350 feet the way the apparatus travel. |