(140) Division of Fire Review  11/05/2007 11/21/2007 11/07/2007 CMTS  Rastegar, Abdol Russell 
Comments:

FIRE - RASTEGAR, RUSSELL

Hydrants must be within a 350-ft. hose lay of the building circumference, a minimum of 50 ft. from the structure wall and accessible to fire department apparatus. Measure hose as laid from apparatus.

Additional Comments ADDITIONAL COMMENTS:
1-     Please verify the location of the DFH for our review.
2-     Please verify the location of the FDC for our review.
3-     Please submit ISO Calculation to see how many FH is required.
4-     Please show the location of FH.
5-     Max. hose lay shall not be more than 350 feet the way the
apparatus travel.